THE ACCURATERELOADING.COM GUNSMITHING FORUM


Moderators: jeffeosso
Go
New
Find
Notify
Tools
Reply
  
Any Electricians here?
 Login/Join
 
one of us
Picture of Toomany Tools
posted
Need some help. My compressor motor burned up on Saturday; 7.5hp, single phase, 3490 rpm. I ordered a replacement, a Baldor 7.5hp, single phase, 3450rpm, advertised as made for compressors. Went to install it and found new motor is not wired the same as the old one. Original motor had 6 leads but replacement only has 4. Two extra leads I figure are to energize "latch" on thermal protection contact in compressor control box. Without that latch the pressure switch doesn't get voltage and motor won't turn on. Anyone have any idea how to wire this?


John Farner

If you haven't, please join the NRA!
 
Posts: 2946 | Location: Corrales, NM, USA | Registered: 07 February 2001Reply With Quote
One of Us
posted Hide Post
There should be a schematic somewhere......in the box or on the motor lead cover. Without seeing the schematic I can't really help.....

I'll bet you can Google the specific motor and find a schematic online.

.
 
Posts: 42463 | Location: Crosby and Barksdale, Texas | Registered: 18 September 2006Reply With Quote
one of us
posted Hide Post
There should be a schematic on the inside of the junction box cover on the motor.
 
Posts: 2443 | Location: manitoba canada | Registered: 01 March 2001Reply With Quote
One of Us
Picture of speerchucker30x378
posted Hide Post
quote:
Baldor 7.5hp, single phase, 3450rpm


https://www.baldorvip.com/serv...nfoPacket/L1509T.pdf


When I was a kid. I had the stick. I had the rock. And I had the mud puddle. I am as adept with them today, as I was back then. Lets see today's kids say that about their IPods, IPads and XBoxes in 45 years!
Rod Henrickson
 
Posts: 2542 | Location: Edmonton, Alberta Canada | Registered: 05 June 2005Reply With Quote
one of us
Picture of Toomany Tools
posted Hide Post
Problem is there were 6 leads and the new motor only has 4. Baldor spec sheet indicates two more leads would be there if the motor had a thermostat, but this one doesn't. Two leads on the compressor go to the controls. Controls don't work with those two leads disconnected. I think if I want to use this motor I need different controls.


John Farner

If you haven't, please join the NRA!
 
Posts: 2946 | Location: Corrales, NM, USA | Registered: 07 February 2001Reply With Quote
One of Us
Picture of speerchucker30x378
posted Hide Post
coffee Sorry John. But wiring diagrams are like women. I know where to find them. But I'll be damned if I have ever been able to understand them !


When I was a kid. I had the stick. I had the rock. And I had the mud puddle. I am as adept with them today, as I was back then. Lets see today's kids say that about their IPods, IPads and XBoxes in 45 years!
Rod Henrickson
 
Posts: 2542 | Location: Edmonton, Alberta Canada | Registered: 05 June 2005Reply With Quote
one of us
Picture of Toomany Tools
posted Hide Post
I figured it out. The two leads that were on the original motor were for a thermostat, normally closed. Controls would disconnect the power if the motor got too hot. All I have to do is connect the two leads I have left over after connecting the motor, and it will provide "latch' voltage for the contactor. I never had the original motor, in ten-years of operation, shut off due to temperature so I doubt I need that feature anyway. Thanks for all the inputs.


John Farner

If you haven't, please join the NRA!
 
Posts: 2946 | Location: Corrales, NM, USA | Registered: 07 February 2001Reply With Quote
One of Us
Picture of Dulltool17
posted Hide Post
John- as long as the sheeves (I'm assuming you have v-belt drive) are still the original ones and nothing else has changed mechanically, you shouldn't have thermal issues.

Sure, there's some risk, but very minimal, IMO.


Doug Wilhelmi
NRA Life Member

 
Posts: 7503 | Location: Texas Hill Country | Registered: 15 October 2013Reply With Quote
One of Us
posted Hide Post
The new motor probably has the thermal protection built it. It should have a tp on the nameplate.
Don
 
Posts: 1086 | Location: Detroit MI | Registered: 28 March 2006Reply With Quote
One of Us
posted Hide Post
Did the old motor actually burn up? Maybe the motor was fine and the thermal switch opened up and disabled the controls. If it did burn up, then the thermal switch wasn't working anyway.
 
Posts: 871 | Registered: 13 November 2008Reply With Quote
one of us
Picture of Toomany Tools
posted Hide Post
Judging by the extremely loud humming noise and the copious amount of magic smoke that came from the motor, I'm certain it was not the thermal switch. Besides, if the thermal switch opens it opens the contacts removing all power from the motor so there would be no humming nor smoke. New motor runs nicely.


John Farner

If you haven't, please join the NRA!
 
Posts: 2946 | Location: Corrales, NM, USA | Registered: 07 February 2001Reply With Quote
  Powered by Social Strata  
 


Copyright December 1997-2023 Accuratereloading.com


Visit our on-line store for AR Memorabilia